i have APC UPS SU2200INET...few days back i was just experimenting when something went wrong and all the settings were changed. although i managed to reconfigure almost all but few still left. if someone having SU2200INET UPS, following settings are required.
the process is
1. connect comm port of your computer to the comm port of ups via serial cable.
2. open hyper terminal or putty, data rate/speed 2400 baud, data bits 8, stop bit 1, parity bit none flow control xon/xoff.
3. once terminal appears press shift+y, SM will appear. press 1 twice with a gap of 3 seconds, prog will apear.....
4. now press 4 and note the value,
5. press 5 note the value,
6. press 6 note the value,
7. press 0 note the value
8. press b note the value...
9. press shift+r,,bye will appear. close the terminal window.
and kindly update the noted data...i am in real trouble.