Done with installation of both units on Saturday. Dawlance official installer didn't show up so i got services of private technician. following steps have been followed
Applied liquor spary on tubes of both outer and inner units for rust prevention.
Pulled the vacuum on line sets for 30 minutes using vacuum pump.
observed the vacuum level for 10 minutes
Released about 100 PSI pressure & joint were tested for leaks with soap water.
I've tested one unit for about 30 minutes. Door and windows were open and tempreature was set on 17C. Amperes started from 0 and gradually increased to 2.7. then came back to 2.2 after five minutes and remained constant on 2.2 for rest of 25 minutes. Outdoor temperature was 29C. I think it should consume max amperes (4.6) until the set temperature achieved but don't know why it stayed on 2.2. Maybe it was running on econo mode(I'm not sure) or adjusted itself according to outdoor temperature. I've not tested the 2nd unit yet. Technician will perform another leak test on running AC as it was not done due to electricity failure. I'll be able review it by end of April after shifting to that house.