yesterday (10th June, Lahore), ΔT was 20.2C (intake temp 31.1C. vent temp 10.9C) (at turbo, not at fan speed 5, because as you increase air volume ΔT decreases, so fan speed is important while comparing ΔT), at max ΔT I got was 22.5-23C otherwise it generally stays in the 20C range, and 22-23C is generally in low latent load conditions, with high latent load (absolute humidity at +-15g/m3), it goes down to 20C approx
and 20C is generally considered satisfactory
(I have same T3 pro 1 ton, with exact half the air volume of 2ton, 550m3, your vent stats can be compared with mine)
set tcl aside, in your case, I can't understand why even kenwood ΔT is at 14C (assuming kenwood is in top notch condition)
because in my books, ΔT if not 20, at least 18-17 is acceptable if the unit is old or repaired etc
but your kenwood is at 14C
tcl at 13.6C
something is wrong with both acs in my opinion
Edit 1, today (11th June) tested again (evening)
outside temp, 35C
temp in the room before turning on ac, 33.5C, relative humidity at approx 55%
15 mins after start, up to 30 mins and onwards, ΔT was 18-18.2C throughout
intake temp, 29.9-30
vent temp, 11.7C
stable instantaneous power consumption, 1325 watts
Fan speed, Turbo
Edit 2: (at night), Outside temp is 32C
ac is consuming 290 watts/1.2 amps
fan speed, full (one step lower than turbo)
room/intake temp, 29.5
vent temp, 18.8C