Once you buy a UPS system then either it 2000 Watt UPS or can be 3000 Watt UPS. Now this figure of 2000 Watt or 3000Watt simply tells you that how much load UPS will bear before it will beep and shutdown because of over load condition. This limit is adjustable in local UPS and it is advised that whenever you buy a UPS system then test it against maximum load condition. Calculate it and make sure UPS shuts down once load is increased beyond its designed capacity. Like UPS shops have different bulbs with different load on a self made test bench, they will turn on 500 Watt bulb, then few of 100 Watts and correspondingly one of 1000 Watt. I hope you got the idea. One more thing, maximum load for which UPS has been designed for should also correspond correctly with batteries sets you are using.
Don?t confuse things as yet I have not replied to your query.
Whenever UPS is installed then its line is kept separate so that you don?t end up damaging UPS system or any electrical device. Now in order to find the maximum load which you have kept on UPS system, turn on all the electrical equipment which are on UPS while its being in backup mode. Take an AMP-Meter similar to that as shown in image and find how much current the your load is drawing by placing meter on wiring going on battery terminals. Like if your findings shows that on maximum load UPS is drawing 70 Amperes from the batteries then note it down and also measure the Voltage across the battery terminals at that instant and suppose it comes out to be 23 Volts considering your UPS has two batteries connected in series.
Now we know Power P=VI, so in this case Power1 = 70 * 23 = 1610 Watt. -----------------------A
I got my first reading and now moving onto the second. Once batteries have became fully discharged after load shedding and light comes back and entire load goes onto the WAPDA while batteries starts to charge. Use AMP-meter and calculate the current on which batteries are being charged and consider it comes out to be 16 Amperes and then measure the Voltage and it comes out to be 26 Volts then we know
Power needed by the UPS to charge the batteries are Power2= VI=26 *16=416 Watt-----------B
So now we have our two readings, where we know that maximum load we have kept on UPS line and maximum load that UPS will take to charge the batteries so final value will be
Power= P1 +P2 =1610 +416 = 2026 Watt, so 3000 Watt generator in this scenario should comfortably handle your UPS (batteries while they being charged) and load connected with UPS line but being switched over to WAPDA by UPS.
I hope this will help