There is no harm is learning things as I know you are worried about your batteries and this is how people learn. In longer run, once you will be through with this process then you will be guiding many. If you cannot afford a AMP meter then at least you should have a good Multi meter as this is a very important tool in diagnosing problems. Every house should have one Multimeter and you can buy a good one for Rs 1000.
TEST CASE: 700 KVA UPS with one 140 AH battery.
I would move ahead by highlighting different scenarios
SENARIO 1:
If gravity of your batteries were nil before then may be your batteries already had some Acid inside it and batteries were already dead that why it could not generate the required gravity on Charging.
But since you told me that CG was nil in all the cells then most probably your batteries are fine and this flush would be very helpful.
SANARIO2:
Gravity was nil before because quantity of Sulphuric Acid was very low inside your batteries in all the cell. Since batteries were never dried in past so I can assume that they are still in tip top condition. Now since all the cells have the same gravity of 1270 so this indicates good news.
YOUR UPS NEEDS SOME ADJUSTMENT
Put your batteries back on charging with caps open as this is a precaution against building of gases inside the batteries. With charging rate 14.1 AMPS, it is abnormal for UPS to keep charging your batteries for 36 hours. Now call your UPS guy and ask him to test the following and note down the measurements.
I believe that while adjusting the charging rate he has disturbed many other parameters in UPS.
1) Check the terminal Voltage of the batteries as UPS should immediately stop charging the batteries once this reaches 14 Volts. This can only be verified once UPS has been charging the batteries for 6-7 hours and you expect that by now it should have been charged. Once your UPS guy adjusted the charging rate then he would not have inspected the Cut of Voltage. You can test this using Multimeter or Voltmeter.
2) Ask him that he can play around with charging rate which he can reduced it to 10 AMPS during adjustment if required. But should not exceed 14 AMPS.
3) Normally Adjustment of UPS require a BAD battery and GOOD battery
4) Against good battery, you look for a cut of Voltage during charging at 14 Volts. Also note the output Voltage of UPS at this instance.
5) Against Bad battery, you look for âShut down of UPSâ once terminal Voltage reaches 10.5 Volts. Also note the output voltage of UPS at this instance.
6) Tell him to perform a load testing on UPS if it shuts down once load is exceeded the capacity indicated in booklet. Very important
7) Tell him to perform a connectivity test if UPS is delivering the required charge to UPS.
I am repeating the same information