Yes The proper Procedure Of Installing SPLIT UNIT Requires You To Vacuum Lines...
Installation Goes Like.....Inner Install....Prepare Line-set....Flare Line-set...Outer Install.....Connect Lineset....Connect Control Wire....
Keep Lenth Of Lineset In Mind....If You Install Longer Lines....
Now There's Another Step Which Is To Install Manifold Gauge And Connect It With Nitrogen Cylinder...Pressurize System Upto 150Psi And Check For leaks...Water SOAP Mixtures Works Good To Detect Any Leak From Joint...Hold It For 10min...If No Pressure Drop LEAK FoUND.....Disconnect The Nitrogen Cylinder And Install Vacuum PUMP And Evacuate System(Vacuum System) Do It For Good 30min Then Lock Down Your Manifold Gauge And Disconnect Vacuum Pump...Hold Vacuum For 10 Min To Make Sure There's No Drop In Vacuum.... You Are DOne Vacuuming
Now If Your Lineset Comes With UNIT And Is Under Standard Length As Factory Recommends In Manual....You Don't Need Additional Gas Charge..For Longer Lineset You Can Read Manual To Charge Gas /FT Additional Lineset Length
If There's No Additional Charge Required...Open Your Service Valve Slowly One By One ...You Need Specific Size L-Key To Do That...
After Doing It ...Start Your Unit And Let It Run For 10min....Measure Readings..And If You Wanna Go One Step Ahead And Double Check For System Performance.....You Need To Measure Superheat Of System( You Can Google How To Do That..Its A Good Long Procedure) Else Disconnect Your Gauges And Tighten All Service Port And Service Valve Caps With Spanner..
If You Need Additional Ref Charge .....Connect Your Manifold Gauge With Charging Cylinder Purge The Line SO No Air Gets In....And Charge Additional Gas Later Measuring On Weight Scale..(In Manual Its Written & You Need To Charge By Weight)