to Saad,
Clean the filters of indoor unit, use air blower to clean out the fins of indoor and outdoor unit; be careful not to touch the fins, they are very easy to bend. Run your air conditioner, when the compressor turns ON, wait 1 minute, measure the temperature of air going into the indoor unit(at the top of indoor unit, from where you can see the air filter), also measure the temperature of cool air coming out of the indoor unit. A difference of 8C and above is what I remember a good difference. For e.g. your measured temperature of air-in is 30C and air-out is 20C, difference 10C. Check and tell.
These splits that we normally use are "critically charged" units. Their charging is based on the Weight of the refrigerant/gas rather than pressure. Physics say Pressure is directly proportional to temperature, so when temperature is high pressure is high and vice versa. Therefore the correct amount of refrigerant is filled in these units by weighing them. Charging by pressure is possible but that requires temperature measurements, pressure measurements(measuring high side pressure mostly not possible on mini-split since there is no service valve port(place to put gauges) on high side), pressure-temperature chart and lastly is not the suggested method of charging for these mini-splits.
First check with soap water if there is leakage at the flare-joints. If no leakage, I would suggest taking the old refrigerant completely out; vacuum and fill again by weight (standard as printed on outdoor unit + compensation for long copper pipes if needed).
Standard weight of the refrigerant is stated on the outdoor unit. Your instruction manual will tell you how much length of copper tube is al-right with the pre-filled refrigerant. Over the standard length(normally 7.5 meter) you will have to add extra refrigerant at the rate of 20gm/meter(might differ in your manual). Use a digital scale, put the cylinder on the scale, read the value, let the refrigerant in the air conditioner until the weight reduces by the amount required.
MHI air conditioners are very good unit, their current input is quite low and the cooling is strong. Their only drawback is that beefy industrial looks! 
Has your unit been not performing well since installation or after sometime of installation?
R-22 is ozone-destroyer, please try your best not to release it in air!