i have just removed one extra time delay.
T1 delay:
this time delay circuit is powered by battery positive coming from s2 switch and negative coming from 14 point relay. ok............
now further extend battery positive and connect to its common point on relay..........
then extend a wire from Normally close of the relay which will act as battery positive for T2 delay...........ok
set its time to 30 seconds....
its function is to disconnect battery positive after 30 seconds.........u got this part right????
T2 Time delay.
it positive is powered by above wire extended from T1 time delay normally close point..........ok
negative is coming from 14 point relay...........
now test T1 & T2 together. both should work simultaneously but after 30 seconds power to T2 gets disconnected........ok
now extend T2 positive and connect it to common point on its relay...........
normally close point connects to petrol solenoid............
normally open connects to flasher circuit..............
the negatives of petrol solenoid and flasher are both connected from 14 point relay......
set T2 time of 2 seconds...................
function: when T2 gets power petrol solenoid is ON for about a second only. as soon as it switches off flasher circuit switches ON.......
now test the whole T1 & T2 in combination. As soon as u give 12 volts. petrol solenoid activates for 2 seconds then goes off. immediately flasher circuit then activates...... after 30 seconds flasher circuit also goes off.........
Hope u got it...........my diagram is correct