I have a 1.2KW Deutsche Power UPS. I am using 2 135Ah Batteries in series, since it's a 24V DC system.
A few days back my batteries went completely dry since i forgot to check the electrolyte level for almost a month. Now when i filled up the batteries and reconnected them to the UPS, i noticed that the UPS never stops charging them. Before this incident, the UPS was running perfectly fine charging the batteries at around 6AMPs.
But now, it does not stop at all and dries up the batteries in just a week. It's currently charging at 11 AMPs with a Voltage of 27.3V at the terminals. Even after a charge of 4-5Hrs the no load voltage of batteries does not go beyond 25.4V (No load voltage is with the UPS removed from the terminals.)
These batteries are more than a year old and i got this UPS about 4 months back. Before this, i was using a locally made UPS which got screwed up and started charging the batteries at 20AMPs.
Any suggestions on what should be done? Should i get the UPS checked or batteries replaced. UPS used to perform exceptionally well before the 'drying up' incident. It used to charge at 2-10AMPs, depending on the voltage of the batteries. But i guess the batteries are never reaching the minimum voltage for the UPS to stop charging.
Btw, i got the gravity checked from a shop and they said that it is 1250.