This is a very informative thread. I was searching for some UPS batteries and came across it.
I have a desi UPS (24 volt) UPS is 1.5Kw. There are 2 batteries Exide 6FT 115 (about 100 AH each). the batteries are about 1.5 years old. Recently when Wapda power goes and UPS comes in action, some appliance do not turn. It seems the current is weak right from the start. Backup time is more than one hour with normal computer, fan and lights.
after reading this thread, i bought a hydrometer and checked the SG of the batteries.
Result of SG
Battery 1. 1170, 1200, 1190, 1180, 1170, 1170
Battery 2. 1190, 1160, 1120, 1130, 1160, 1170
I also noticed that on the batteries the area around the caps was slightly damp. The water was blackish and I noticed some particles also in the water.
I do not have a amp meter or any other metering device for checking the current, so I will ask the UPS guy to come and check the UPS for the readings.
Regarding the battery, i will purchase the electrolyte from PYRO chemicals and do a flush in the coming days. What do these readings mean ? Is the battery ok coz the backup time seems ok only some applicances like the motor in the aquarium starts making noise even if I turn off each and every other thing in the house.